$A$ small town with a demand of $800 \; kW$ of electric power at $220 \; V$ is situated $15 \; km$ away from an electric plant generating power at $440 \; V$. The resistance of the two-wire line carrying power is $0.5 \; \Omega/km$. The town gets power from the line through a $4000-220 \; V$ step-down transformer at a sub-station in the town.
$(a)$ Estimate the line power loss in the form of heat.
$(b)$ How much power must the plant supply,assuming there is negligible power loss due to leakage?
$(c)$ Characterise the step-up transformer at the plant.

Vedclass pdf generator app on play store
Vedclass iOS app on app store
(N/A) Total electric power required,$P = 800 \; kW = 800 \times 10^3 \; W$.
Supply voltage at the town,$V = 220 \; V$.
Voltage at which the electric plant generates power,$V' = 440 \; V$.
Distance between the town and the power generating station,$d = 15 \; km$.
Resistance of the two-wire line $= 0.5 \; \Omega/km$.
Total resistance of the wires,$R = (15 + 15) \times 0.5 = 15 \; \Omega$.
$A$ step-down transformer of rating $4000-220 \; V$ is used in the sub-station.
Input voltage to the transformer,$V_1 = 4000 \; V$.
The current in the transmission line is $I = \frac{P}{V_1} = \frac{800 \times 10^3}{4000} = 200 \; A$.
$(a)$ Line power loss $= I^2 R = (200)^2 \times 15 = 40000 \times 15 = 600,000 \; W = 600 \; kW$.
$(b)$ Total power supplied by the plant $= \text{Power required} + \text{Power loss} = 800 \; kW + 600 \; kW = 1400 \; kW$.
$(c)$ Voltage drop in the power line $= I \times R = 200 \times 15 = 3000 \; V$.
Total voltage transmitted from the plant $= \text{Voltage at transformer input} + \text{Voltage drop} = 4000 \; V + 3000 \; V = 7000 \; V$.
Since the plant generates at $440 \; V$,the step-up transformer rating is $440 \; V - 7000 \; V$.

Explore More

Similar Questions

The primary winding of a transformer has $500$ turns,whereas its secondary has $5000$ turns. The primary is connected to an $ac$ supply of $20\, V$,$50\, Hz$. The secondary will have an output of

$A$ step-down transformer is connected to a $2400\,V$ line, and $80\,A$ of current is found to flow in the output load. The ratio of the turns in the primary and secondary coil is $20:1$. If the transformer efficiency is $100\%$, then the current flowing in the primary coil will be......$A$.

Difficult
View Solution

In a step-up transformer,if the ratio of turns of primary to secondary is $1:10$ and the primary voltage is $230 \, V$. If the load current is $2 \, A$,then the current in the primary is.......$A$.

The coils of a step-down transformer have $500$ and $5000$ turns. In the primary coil, an $AC$ current of $4 \,A$ at $2200 \,V$ is sent. The value of the current and potential difference in the secondary coil is:

$A$ generator at a utility company produces $100 \, A$ of current at $4000 \, V$. The voltage is stepped up to $240,000 \, V$ by a transformer before it is sent on a high voltage transmission line. The current in the transmission line is ....... $A$.

Vedclass Products

For Students

Vedclass Test Series

Mock tests in real JEE/NEET style with performance analysis. 5-day free trial.

Start Free Trial
For Teachers

Exam Paper Generator

Generate Set A/B/C/D exam papers from 7.5L+ questions in 2 minutes. 3 chapters free.

Try Free
For Institutes

Online Exam Module

Live online exams with unlimited students, 360° analytics & white-label branding.

See Demo