$A$ small town with a demand of $800 \; kW$ of electric power at $220 \; V$ is situated $15 \; km$ away from an electric plant generating power at $440 \; V$. The resistance of the two-wire line carrying power is $0.5 \; \Omega/km$. The town gets power from the line through a $40,000-220 \; V$ step-down transformer at a sub-station in the town.
$(a)$ Estimate the line power loss in the form of heat.
$(b)$ How much power must the plant supply,assuming there is negligible power loss due to leakage?
$(c)$ Characterise the step-up transformer at the plant.
(Neglect,as before,leakage losses). Hence,explain why high-voltage transmission is preferred?

Vedclass pdf generator app on play store
Vedclass iOS app on app store
(A) Given: Power $P = 800 \; kW = 8 \times 10^5 \; W$,Voltage at town $V_1 = 40,000 \; V$,Distance $d = 15 \; km$,Resistance per unit length $r = 0.5 \; \Omega/km$.
Total resistance $R = (15 + 15) \times 0.5 = 15 \; \Omega$.
Current in the line $I = P / V_1 = (800 \times 10^3) / 40,000 = 20 \; A$.
$(a)$ Line power loss $P_{loss} = I^2 R = (20)^2 \times 15 = 400 \times 15 = 6,000 \; W = 6 \; kW$.
$(b)$ Total power supplied by the plant $P_{total} = P + P_{loss} = 800 \; kW + 6 \; kW = 806 \; kW$.
$(c)$ Voltage drop in the line $V_{drop} = I \times R = 20 \times 15 = 300 \; V$. Voltage at the output of the step-up transformer $V_{out} = V_1 + V_{drop} = 40,000 + 300 = 40,300 \; V$. Since the plant generates at $440 \; V$,the step-up transformer is $440 \; V - 40,300 \; V$.
High-voltage transmission is preferred because power loss $P_{loss} = I^2 R = (P/V)^2 R$ is inversely proportional to the square of the transmission voltage $V^2$. Increasing $V$ significantly reduces $I^2 R$ losses.

Explore More

Similar Questions

The output voltage of a transformer connected to a $220 \, V$ line is $1100 \, V$ at a $1 \, A$ current. Its efficiency is $100 \%$. The current coming from the line is ........ $A$.

$1\, MW$ power is to be delivered from a power station to a town $10\, km$ away. One uses a pair of $Cu$ wires of radius $0.5\, cm$ for this purpose. Calculate the fraction of ohmic losses to power transmitted if
$(a)$ power is transmitted at $220\, V$. Comment on the feasibility of doing this.
$(b)$ a step-up transformer is used to boost the voltage to $11000\, V$,power is transmitted,then a step-down transformer is used to bring voltage to $220\, V$.
Given: $\rho_{Cu} = 1.7 \times 10^{-8}\, \Omega \cdot m$.

The primary winding of a transformer has $500$ turns,whereas its secondary has $5000$ turns. The primary is connected to an $ac$ supply of $20\, V$,$50\, Hz$. The secondary will have an output of

If a step-up transformer has a turn ratio of $5$,a frequency of $50 \, Hz$,the root mean square $(RMS)$ value of the potential difference on the primary is $100 \, V$,and the resistance of the secondary winding is $500 \, \Omega$,then the peak value of the voltage in the secondary winding will be (the efficiency of the transformer is $100 \%$).

$A$ transformer has $120$ turns in the primary coil and carries $5 \text{ A}$ current. Input power is $1 \text{ kW}$. To have $560 \text{ V}$ output, the number of turns in the secondary coil will be:

Vedclass Products

For Students

Vedclass Test Series

Mock tests in real JEE/NEET style with performance analysis. 5-day free trial.

Start Free Trial
For Teachers

Exam Paper Generator

Generate Set A/B/C/D exam papers from 7.5L+ questions in 2 minutes. 3 chapters free.

Try Free
For Institutes

Online Exam Module

Live online exams with unlimited students, 360° analytics & white-label branding.

See Demo